Power Systems · Problem type
Per-unit impedance
Use this for “On a 138 kV, 100 MVA base, what is a 19.04 Ω line impedance in per unit?”
Diagram
Zₚᵤ = 0.09998 pu on the top line sits over 19.04 Ω on the bottom line: each 1 above is 190.44 below.
This is an example. Type your own values to start a new problem.
Zbase (Ω)
=
(
Vbase (kV)
)
2
÷
Sbase (MVA)
Zₚᵤ (pu)
=
Z (Ω)
÷
Zbase (Ω)
Formulas
Zbase
=
Vbase
2
Sbase
190.44
=
138
2
100
Zₚᵤ
=
Z
Zbase
0.09998
=
19.04
190.44
Assumptions
•
Vbase is the line-to-line voltage and Sbase the three-phase power; Zbase is then the impedance of one phase.
•
A per-unit value is the value over its base, so Zbase itself is 1 pu.
•
With Vbase in kV and Sbase in MVA, Vbase² ÷ Sbase comes out in ohms: the 10⁶ factors cancel.
Step-by-step
WE KNOW
Vbase = 138 kV, Sbase = 100 MVA, Z = 19.04 Ω
FIND
base impedance (Zbase), per-unit impedance (Zₚᵤ)
Step 1 · Find base impedance (Zbase)
Use Zbase = Vbase² ÷ Sbase
The
impedance
that
draws
the
base
power
at
the
base
voltage:
V
2
S
.
Zbase
=
138
2
100
Zbase
=
19,044
100
Zbase = 190.44 Ω
Step 2 · Find per-unit impedance (Zₚᵤ)
Use Zₚᵤ = Z ÷ Zbase
Per unit means a fraction of the base: divide the ohms by Zbase.
Zₚᵤ
=
19.04
190.44
Zₚᵤ = 0.09998 pu
Check
Put the numbers back in. Both sides should match.
190.44
=
138
2
100
✓
0.09998
=
19.04
190.44
✓
Topic check
See what you know: 5 questions on this topic
New questions each time. Pass to mark it complete.
Related lessons
Power flow
Main lesson
Changing the per-unit base
Use this for “A generator is 0.1 pu on its 50 MVA rating. What is that on the 100 MVA system base at the same kV?”
Approximate voltage drop
Use this for “A line with R = 0.02 pu and X = 0.1 pu delivers P = 0.8 pu and Q = 0.6 pu at 1 pu. Find the sending voltage.”
Line losses
Use this for “A 33 kV line carries 10 MW at power factor 0.9 with 5 Ω per phase. Find the current and the loss.”